hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I know their is code ANSI or something else that tell typical transformer % impedance range values based on its size. Does anyone know which code I would find that in?
Is there particular reason you need to know this? We see specs that say no higher than a certain level say 5%.I know their is code ANSI or something else that tell typical transformer % impedance range values based on its size. Does anyone know which code I would find that in?
IEEE.I know their is code ANSI or something else that tell typical transformer % impedance range values based on its size. Does anyone know which code I would find that in?

Is there particular reason you need to know this? We see specs that say no higher than a certain level say 5%.
For other than incident energy calculations, the worst case current is what you want to see.Utility want give so approximate worst case fault current based on transformer size and %z
For other than incident energy calculations, the worst case current is what you want to see.
You get that from the utility ....it is based on the transformers that they use. In fact, normally you get the service fault current from the utility and that is based on the worst case for the types of transformers that they use in their system.Correct in other words other than Arc flash study the worst case is what I want. This lowest possible impedance %z for given sized utility xfmr. So then which code would have that DOE or ANSI? If ANSI then which version?
For first step design, I use 1.2% up to 150kVA, 3.5% up to 300kVA, and 5.0% for larger utility transformers.I know their is code ANSI or something else that tell typical transformer % impedance range values based on its size.
Please in the future mention in the OP that this is a utility transformer.Correct in other words other than Arc flash study the worst case is what I want. This lowest possible impedance %z for given sized utility xfmr. So then which code would have that DOE or ANSI? If ANSI then which version?