we have a trans that is wired in reverse the prim. is 208v and the sec. is 480v. it is suppling power to 2 - 30amp. 480v recept. when checking output i find that there is 480 between each phase lines but to ground there is only 15volts. i know there is a problem with the grounding. there is no connection to the building steel , the trans is just sitting on floor. when the trans was wired up the on the sec. side the elect. installed ground wire from the recept. to the case of the trans. no other ground is there. should he have wired xo on trans.? how do i make this safe ? i plan on installing a #6 from the trans to building steel after that i'm not sure. thanks for any help