Transformer Info
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
First off I want you to know I do not know anything about trany's.
I ran into this and don't understand it.
What is the current on the secondary side of a 75 KVA 3 phase 480:208/120 volt wye transformer?
What does the 480:208/120 mean?
The secondary current is 208 amps (75000 va / 208 volts / 1.73 sq rt3 = 208 amps).
The ratio shows the primary voltage as 480, the secondary as 208 line to line, and 120 line to the midpoint of the wye secondary.
Thank you-- I couldn't understand the colon. I was thinking it was a 480 or 208 tap on the primary and 120 on the secondary but obviously that was dumb thinking. That also explains why I got the wrong answer. :grin:
One of your signature statements serves you well! A colon expression of a ratio!
:grin:
http://mathworld.wolfram.com/Colon.html
Yeah I know what a colon is. Someone was here with me and somehow I just look at it in a bizarre way. Again I'll blame the drugs but to be honest I had never seen a trany written as a ratio. Obviously I am a bit inexperienced with tranys. Except for a few door bell transformers I believe I have hooked up less than 3 in my life and all of them were very small.:grin:
And Jude-- I am good at fractions....:grin: I am also good at sarcasm
A transformer is used to transfer energy from one circuit to another. It can provide isolation between the systems and a change in voltage levels or both.
:grin:
In this case, it replaces the word "to".
A 480 to 208Y/120 transformer.
Yes, I still cannot believe I didn't see that but hey- c'est la vie.
Thanks -- just when I think I have gotten real good at this code stuff I always get put in my place.:grin: