I have a customer with a 200 A Single Phase Service and he has a 50 KVA,240 (sec.) to 480 (pri.) Single Phase Transformer.
The customer needs single phase 480 V for machinery he has for his shop.
My question is as follows:
Is a 200 A Service enough supply or VA to handle the inrush current of the 50 KVA Transformer?
If my calculations serve correctly (as far as sizing the breaker size for the primary of the transformer), I would need the following primary feeder breaker:
Ampacity of Breaker = Transformer KVA/Transformer Pri. Volts/1.73
= 50 KVA/240 V/1.73 = 120 A
The breaker that is currently feeding the 50 KVA Single Phase Transformer is 100 A (2P, 240 V).
Customer said he closed the 100 A Breaker feeding the 50 KVA Transformer and it tripped instantaneously.
Now, if my calculation of breaker size is correct then this should work, right?
I work for a third party testing agency and it is in my experience that Molded-Case Breakers typically trip around 5-10x Breaker Current Rating.
If the customer's 100 A Breaker is tripping instantaneously, wouldn't that mean he has 500-1000 A (or more) tripping the breaker?
Any help would be appreciated, thanks.
The customer needs single phase 480 V for machinery he has for his shop.
My question is as follows:
Is a 200 A Service enough supply or VA to handle the inrush current of the 50 KVA Transformer?
If my calculations serve correctly (as far as sizing the breaker size for the primary of the transformer), I would need the following primary feeder breaker:
Ampacity of Breaker = Transformer KVA/Transformer Pri. Volts/1.73
= 50 KVA/240 V/1.73 = 120 A
The breaker that is currently feeding the 50 KVA Single Phase Transformer is 100 A (2P, 240 V).
Customer said he closed the 100 A Breaker feeding the 50 KVA Transformer and it tripped instantaneously.
Now, if my calculation of breaker size is correct then this should work, right?
I work for a third party testing agency and it is in my experience that Molded-Case Breakers typically trip around 5-10x Breaker Current Rating.
If the customer's 100 A Breaker is tripping instantaneously, wouldn't that mean he has 500-1000 A (or more) tripping the breaker?
Any help would be appreciated, thanks.