Hello all, new contractor here. I have a three phase 480v 3 wire panel. I'm doing a transformer job with a 45kva transformer which will step down to 120/208v. the distance from the main distribution panel is 250' away. I'm using a 70amp breaker with 6awg and a EGC #8awg in a 1" raceway for the primary side. The secondary calculations are as follows: transformer protection size is 150amps 1/0 awg with a 6awg SSBJ in a 2" conduit. 
Questions that I have are:
1- NEC requires a disconnect and then into the transformer correct? and if so how would I size that? do I size to the primary or secondary voltage? also how many amps would I size it to?
2- coming out of the secondary to the new panel I understand I need to terminate to a over current protection device. will it be okay to come into a 125amp sub panel being that my conductor ampacity would be 150amps?
	
		
			
		
		
	
				