Is it true that transformers are rated to run continuously at 100% of their rated kVA?
In other words if I had a transformer with a secondary current output of 100 amps could connect 100 amps of continuous load to that transformer? (Not that I would but is it rated to handle that volume of current continously?)
The reason I am asking is this. I was told that transformers were rated to run continuously at their kVA rating. So if I had a transformer with a rated output current of 100 amps and protected the secondary at 125% using a 125 amp circuit breaker and connected the maximum allowable continuous current (100A) to the panel it supplied, the system would be legal and functional. Is this true?
In other words if I had a transformer with a secondary current output of 100 amps could connect 100 amps of continuous load to that transformer? (Not that I would but is it rated to handle that volume of current continously?)
The reason I am asking is this. I was told that transformers were rated to run continuously at their kVA rating. So if I had a transformer with a rated output current of 100 amps and protected the secondary at 125% using a 125 amp circuit breaker and connected the maximum allowable continuous current (100A) to the panel it supplied, the system would be legal and functional. Is this true?