steveng:
First, you need to define the primary voltage.
Inrush current is a random value from near zero to some maximum value and varies over this range depending on the point in the AC cycle that turn on occurs and the last magnetic residual state of the transformer core.
If there is a load on the transformer, then this adds to the inrush current. If you had an all incandescent load you might have 10 times the initial current from these lamps that you have for their steady state conditions.
Worst turn on time point for incandescent lamps is near the peak of the voltage waveform.
Worst turn on time point for the magnetic core is a voltage point such that the volt-time integral causes the magnitude of the core magnetic flux to increase from the residual flux state. This quickly puts the core into saturation. You need to be familar with hysteresis curves of magnetic materials to understand this problem.
The source impedance in the supply to the transformer will have a significant effect on peak inrush current.
You might expect a peak inrush current from 5 to 20 times the full rated transformer primary current. Very dependent on the various factors mentioned. In a worst case with no secondary load the maximum possible current in the primary is determined by the source voltage, source impedance, and the DC resistance of the primary.
For the most part this is an 8 to 16 MS transient.
Jim will probably give you a simpler answer, but if you can follow the theory, then you can reason a similar problem for yourself in the future.
.