The secondary of a Delta-Wye transformer will be 30? out of phase with the secondary of a Delta-Delta transformer. If the tranfer scheme is closed transition you cannot use two sources 30? out of phase.
"The transformer will be used in an 83 throw-over scheme with an existing delta-delta transformer. "
What does this mean?
The transformer will be used in an 83 throw-over scheme with an existing delta-delta transformer. .
........... If the tranfer scheme is closed transition you cannot use two sources 30? out of phase.
Lets say I am measuring the voltages on the 83 (transfer switch).
SOURCE 1
L1 to L2 = 230V
L2 to L3 = 230V
L1 to L3 = 230V
SOURCE 2
L1 to L2 = 230V
L2 to L3 = 230V
L1 to L3 = 230V
If I were to measure between Source 1 Line 1 & Source 2 Line 1 how much voltage appears on the meter ? A 30 degree phase shift between the sources exists.
Can I just use the COS of 30 & come up with 31volts ?
Was the secondary voltage of the received transformer ever stated?
Is it 208Y/120 or is it 230Y/133?
It seems odd if it came in at a line-line voltage of 230 when wired delta-wye, no?
Edit: I guess since it's going to another country???? Which country and what's their standard voltage?
USe the 2x (SIN15) and you get 119 volts.
Are you parelling the two sources? If not what difference does the phase shift make?
Are the utility sources in phase? If not adding a phase shifting transformer would bring then in phase at point you want to transfer. It would make it possible to make a closed transition. This should be an easy question to answer, not seeing everything is leading to lots of guesses. Gotta drawing of the system?//
That is what I keep saying, everyone is just worried about the grounding. Hope someone listens to you.
This stuff is way above my head but check the last page of this PDF out.
http://ecatalog.squared.com/pubs/Electrical Distribution/Medium Voltage Transformers/7400DB0701.pdf
That's my computer shut-down sound: "Where's the ka-boom? There's supposed to be an Earth-shattering ka-boom!"Let's just hope there is not going to be an earth-shattering Kaboom!!
The transformer was special ordered with a 230 volt L-L secondary. The engineer thought he was ordering a delta-delta. It may be that the supplier is at fault.
The country is Canada.
I have no idea of their standard voltages.
Our standard voltages are 600/347, 240/120, 208/120. The NEC may not apply but the CEC will and the provincial codes as well. I'd make sure everything is stamped CSA as well, inspectors really like that.
USe the 2x (SIN15) and you get 119 volts.
Are you parelling the two sources? If not what difference does the phase shift make?
Are the utility sources in phase? If not adding a phase shifting transformer would bring then in phase at point you want to transfer. It would make it possible to make a closed transition. This should be an easy question to answer, not seeing everything is leading to lots of guesses. Gotta drawing of the system?//