Am I correct that the amount of (apparent) power you can push through a transformer is actually less than the transformer's nameplate rating because you have to consider the losses of the transformer?
That's something I hadn't really considered before. I always mentally assumed you could put 10MVA through a 10MVA transformer. And so if you wanted 10MVA on the secondary side, maybe you'd be up >10MVA on the source side, but you'd still be under the damage curve by design. But thinking through this, I'm wondering what is true. Are you actually limited to strict nameplate size on the source side such that max MVA delivery is actually nameplate minus transformer losses (including var consumption)?