toireht
Member
- Location
- port allen, la, usa
looking at existing installation of a transformer. transformer is located in building with 480 volt system. transformer is 37.5 kva. 2 hots off 480 system and ground ran to primary side. h2 and h3 connected together. hots to h1 and h4. the secondary side actually runs to detached trailer. secondary is 4 wire, hots on x1 and x4, x2 and x3 connected together with neutral. the ground from the primary side and secondary side are connected to transformer frame and to ground rod near transformer. trailer has a meter with circuit breaker disconnect. hots connect to line lugs and neutral connects to neutral bus that is bonded to ground. ground wire connects to ground bus. Is this proper set up? should the bonding of the neutral be done at transformer or is it ok at meter panel on trailer? only one bounding of neutral to ground is allowed? trailer is 25 feet from building with transformer. about 30-35 feet of wiring. trying to determine if we need to redo this installation.