This is the nameplate of a transformer that is to feed a piece of equipment. The secondary feeder will land on a 160 amp breaker that feeds the equipment. The engineer that has designed the install, has sized the transformer to its max capacity and is requiring feeders much larger than 160 amp. I physically do not have enough space to do this however; he insists that the conductors must be sized to the nameplate of the transformer. Call me crazy, but there is nothing that requires me to use 100% of the transformer and I should be able to size my secondary conductors off of the 160 amp breaker, correct? no other loads will be fed by this transformer. He is also insisting that the primary conductors would be sized for 270 amps which is 125% of the nameplate. But again, if Im not using the transformer to its capacity, am I required to have OCPD and conductors sized to the nameplate?