Transformer not used to capacity

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Yup but remember you can round up to the next higher standard ocpd rating if under 800a

Sent from my A574BL using Tapatalk

only on the secondary side.

I believe that is incorrect. 240.21 (C)

(C) Transformer Secondary Conductors. ....... The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.

Next size up on primary is OK, not on secondary
 
I believe that is incorrect. 240.21 (C)

(C) Transformer Secondary Conductors. ....... The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.

Next size up on primary is OK, not on secondary

There may have been some confusion about the transformer protection vs conductor protection. In post #17 I was referring to transformer protections. I understand Bobs response now.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
I believe that is incorrect. 240.21 (C)

(C) Transformer Secondary Conductors. ....... The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.

Next size up on primary is OK, not on secondary
Is that 2017? My 2014 doesn't have a section C. WI is still on 2011 lol

Sent from my A574BL using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is that 2017? My 2014 doesn't have a section C. WI is still on 2011 lol

Sent from my A574BL using Tapatalk


In 2017 it's on Pg 97, in 2014 it's on Pg 99.
You must have a special DrSparks addition :D
 