Isn't that the Table 450.3(B) allows us to do that " Primary only protection" ?The secondary conductors still need to be protected per article 240, so you can't completely eliminate the OCP on the secondary, if that is what you are asking.
Isn't that the Table 450.3(B) allows us to do that " Primary only protection" ?The secondary conductors still need to be protected per article 240, so you can't completely eliminate the OCP on the secondary, if that is what you are asking.
450.3(B) covers protection for the transformer, but you still need to protect the transformer secondary conductors per 240.21(C).Isn't that the Table 450.3(B) allows us to do that " Primary only protection" ?
Yes i am and to satisfy the 240.21(C) and 450.3(B) , shouldn't the primary OCP be 225A ( 250%) and secondary OCP be 250A (125%) ??450.3(B) covers protection for the transformer, but you still need to protect the transformer secondary conductors per 240.21(C).
Assuming you are still talking about a 3 phase transformer (like the original post), you still need secondary protection for the conductors.
Secondary protection is optional per 450.3(B). There is no requirement to upsize the primary based on a secondary protective device.Yes i am and to satisfy the 240.21(C) and 450.3(B) , shouldn't the primary OCP be 225A ( 250%) and secondary OCP be 250A (125%) ??
take a look at the primary protection requirements in the cases where no secondary protection is required.Isn't that the Table 450.3(B) allows us to do that " Primary only protection" ?