I work as a maintenance electrician in metal foundry, started in April, and I have a question concerning an existing transformer that I believe the OCPD is not properly sized.
It is a 100kva single phase transformer with primary voltage of 480vac and secondary voltage of 240vac. The secondary is feeding a panel, less than 10ft away. The panel has 200amp main with 17 of the 20amp breakers being used out of the 40 available slots.
The transformer primary is being protected by a 100amp breaker in a 400amp protected power distribution cabinet. My calculations for primary only protection show that this transformer should be protected by a 300amp OCPD.
Am I missing something to where the 100amp breaker is adequate protection?