That is clear under 2023/2026 NEC 705.30(F). But 2020 NEC 690.9(D) sometimes required considering it primary for compliance with 450.3. So when discussing 690.9(D), it is more clear to stick with inverter side and utility side.The inverter side of a 480/277V wye to 208V delta interconnection transformer is the secondary.
Cheers, Wayne