From their specifications:
So they have 5 x 1kW (3/4HP) single phase motors on this thing, but they are rating the motors at 50 OR 60Hz. That is not going to be true, there has to be some sort of compromise here, so they are just not willing to allow any further "fudge factor" in the field because they are already using it rather sell two different versions for 50 or 60Hz markets. The thing is, YOU have no control over what the utility actually gives you, meaning it might be 244V today, but it might be 238V tomorrow.
So I would document the ACTUAL measure voltage at the time of installation, select and install a Buck-Boost transformer to get you as close as possible, and tell your customer that this is the best available option but make no assurances beyond that.
I see 5 turbine motors with a total of 3 kw. I wonder if this is a listed product. It must be as they are located all over the country
General:
· External cylinder diameter: 37" (940mm)
· Rated Load: 450 lbs. (205 kg)
· Number of Stops: 3
· Speed: 30 fpm
· Travel 1-2 & 2-3: TBD
· Color: White
· No pit required. Bottom level floor must be 100%
level as elevator rests on existing floor.
· Overhead clearance.: 97" Min
· No hoist way required.
· Penetration required to install through floors and
ceilings: 39” (991mm)
Safety:
· Automatic descent to ground level at safety speed in the
event of a power failure.
· Mechanical emergency brakes within two inches of free
fall in vacuum loss or catastrophic failure.
· Electromechanical interlocks at each landing
· Alarm system and telephone
Certification:
· American Society of Mechanical Engineers ASME A17.7
· See Supporting certificate and report
· Certificate # NA 10-0842-1004-003-01
Cabin:
· Entrance width opening: 23 1/2 " (569.9mm)
· Internal cabin height: 79" (2006mm)
· Internal cabin diameter: 32" (812.8mm)
· Automatic LED lighting and cabin fan
· Door openings: Inline Side
o All doors are hinged on top left, with door swing to the
left, from inside the cabin.
§ Door Height: 77" (1,956mm)
§ Height to top of Door closer: 79" (2006mm)
o Each landing level specified will include only one door.
· 24 Volt electrical circuits with all controls in cabin
· Push button call controls with precise leveling at each landing.
Mechanical Requirements:
· 220V, 60/50 30amp single phase power supply
·
5 Turbine motors located in pump box using a total of 3KW
Load Calculation:
Given load on ground floor is based on a car full load of 450
lbs, brake anchoring, and momentum / stress under braking.
Load is 93 PSI. ( Note: Given load is when car is at top floor
landing and resting on column / railing). Load is transmitted
vertically to ground floor via column/rail.
The dimension of each column is 3.2" X 1.68"