elmundogrande
Member
Let’s say: I have a 30 KVA step-up transformer 240 to 480 volts and no mention of thermal overloads. Using table 450.3B with primary and secondary protection is going to be used 30000/240v= 125A x 250% = 312.5 according to the table I can’t use the next size up not using x125% and no mention of thermal overload so a 300a ocpd is needed.