16.2.2.2 Lighting circuits shall have overcurrent protection in accordance with 7.2.6 and shall be supplied from one of the following sources:
(1) A separate isolating transformer connected to the load side of the supply disconnecting means. Overcurrent protection shall be provided in the secondary circuit.
(2) A separate isolating transformer connected to the line side of the supply disconnecting means shall be permitted for the supply of a maintenance lighting circuit in control enclosures only. Overcurrent protection shall be provided in the secondary circuit.
(3) A grounded machine circuit that has separate overcurrent protection and does not exceed 150 volts to ground shall be permitted.
(4) An isolating transformer connected to the line side of the supply disconnecting device when a separate primary disconnecting means and secondary overcurrent protection are provided and mounted within the control enclosure adjacent to the supply disconnecting device.
(5) An externally supplied lighting circuit (e.g., factory lighting supply). This shall be permitted in control enclosures and for the machine work light(s) where the total power rating does not exceed 3 kW.
7.2.6 Lighting Circuits. . Overcurrent protection for lighting branch circuits shall not exceed 15 amperes.