@Phil,TopGone...
While you seem to have no interest, others may be interested! So, here is the conclusion of my analysis: V-drop, across the transformer is in the order of 13%, not 23%!
Parameters used:
o Running-load is 150kVA (1/2 Xfmr Rating) @ 0.8 pf.
o Pump motor locked-rotor inrush is 600kVA @ 0.3 pf (4x motor rating).
o Resultant connected-load is ~ 730kVA @ 0.6 pf ( 2.4x Xfmr rating).
o Xfmr: kVA, 300; %Z, 4.75; Pcu, 4,000W @ FL; Pfe, 400W @ FL.
o % V-drop for running-load is ~ 2%.
o % V-Drop for combined loads is ~ 13%.
Regard, Phil
ThatMan ran his ETAP software and got 78% VD. I did my own calcs and got 77%. The thing is, you were using 750kVA as the transformer load. ThatMan posted the total load to be 900kVA (though this is a starting duty only).