What Augie said. Back to the drawing board.
As for Transformer protection 450.3Sorry, can I ask you what code section this is so I can read about it more.
So the Panel can be sized for 600AMP but the total demand load still needs to be around 400AMP only
Based on Table 450.3(B)As for Transformer protection 450.3
As for conductor size (secondary) 240.21(C)
I wouldn't have interrupt the table that way. I would have make the primary 250% and the secondary be protected by 125%You can exceed that 125% primary and go up to 250% but, if you do so, the secondary would need to be protected at 125%
From what I have read in the code, (240.21(C)(1)), on this type of transformer (delta to wye)you will always be required to have secondary protection.You somewhat answered your own question
The transformer can be protected by primary protection only if that protection does nor exceed 125% pf the primary current.
In your case that would be 169 amps and the breaker is 150 amp so it is within the 125% allowable range.
It allows a 175(next size up) but doesn't preclude any lesser value.
Anything less than 175 and the transformer is considered to be protected.
You can exceed that 125% primary and go up to 250% but, if you do so, the secondary would need to be protected at 125%
I get your point. But what you gave to the OP was not a correct response as you can clearly see that his question was about a transformer that requires secondary protection.I was referencing Art 450 Transformer protection only....
Trying not to muddy the water
I agree Art 240 requires secondary protection and Art 408 requires line side protection on the panels but I was attempting to shed light on Art 450 without going further.
(you are correct...I should have prefaced my comment with 'as far as Art 450 is concerned' )
Is it the transformer itself that requires the secondary protection or is it the secondary conductors that require the protection?I get your point. But what you gave to the OP was not a correct response as you can clearly see that his question was about a transformer that requires secondary protection.
Not really.When combing both Art 240 and Art 450, all transformer need primary and secondary protection.