If the transformer has impedance of 6%, then:
I,fault = 500/(1.732 x 4.16 x 0.06)=1.16 kA
Now should it be: Z,ohm= 4.16/1.16=3.59 Ohm
Or should it be: Z,ohm=4.16/(1.732 x 1.16)=2.07 Ohm ?
Can we usually ignore the utility impedance for cable sizing?
Also is this cable sizing method valid for all cables (LV, MV, and HV)?
Thanks
line to line fault (which is typically larger than l-g so should be used for sizing) is the 3.59 Ohm
the 2.07 is your single line equivalent Z (mult by 1.732 to get phase)
Z base = (4160)^2 / 500000 = 34.61 Ohm
Z act = 0.06 x 34.61 = 2.077 Ohm (single line equiv) or 3.597 phase (call it 3.6)
this is not used for sizing the cable but determining a fault current magnitude
the utility impedance will
lower the fault current so it can usually be ignored unless you need a lower fault current so you can use lower rated equipment if the infinite bus puts you on the border of 2 sizes, typically does not change things much
if you want to estimate line Z influence:
assume 3% Vdrop (Vd) (can be 2% for short runs, whatever you feel is appropriate)
Vll = phase V
I full load Ifl = kva/(1.732 x Vll)
plugging and crunching
Vd = 0.03 x Vll = Ifl x Z (If)
Z = 0.03 x Vll^2 x 1.732 / kva = 0.03 x 4160^2 x 1.732 / 50000 = 1.798 Ohm (call it 1.8)
new fault current
= 4160/(3.6 + 1.8) = 0.77 kA (reduced from 1.16 kA by considering the conductors)