timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
A question about using transformer in opposite direction. For example a 500 kVA 13.8/4.16 kV transformer to be used as 4.16/13.8 kV. Originally the current on the 13.8 kV side was 20.9 A. But when used in the opposite direction, the current on the original 13.8 kV side would become 69.4 A (3.3 times more). As the winding on this side is not designed for this higher current, so we should keep the new load 3.3 times less than 500 kVA. Should we now use a fuse in series with the upstream relay in order to keep the let through current 3.3 times less? Thanks for help.