I know this is a NEC blog, but we seam to have some brite people here. I have a small commercail building with 2 30 HP hydrolic elevators. The elevator company started up elevators today and I got a call from from one of my guys that when they start the elevators the temp lights go out. I took a ride over and checked it out, I have a 800 amp 480 volt service and feed a 300 kVA transformer and the lights an phase A go out for a second phase B blink a bit and phase C looks good. checked the voltage and currant and at 208 start up the voltage drops to about 160 AB and 190 BC the currant looke even and the top of the swing of the analoge meter was about 175A. Opened the transformer checked the pri voltage and was rock solid, phase A to ground was 90 phase B 120 phase c was 122 and with out the start up all were 122. Took the reading with a Fluke scope meter set for voltage trend.
Checked the taps all the same and all tight The Y is welded solid, and I have no clue? any buddy have any ideas.