Hi,
I have a 2500KVA, 13.8kV - 480 V, delta/star neutral solid grounded transformer. It is protected by a MV breaker on the upstream and closecoupled to LV main breaker on the secondary side. The trafo is also provided with a temperature monitor device which can send alarm/trip signals based on the sensor. But, the device comes with only one set of contacts by which I could trip either MV bkr or LV bkr but not both.
My question is, what is the safest way of protecting the system? Additional contacts on the temp monitor device can be obtained but at an additional cost. Is it a common practise to trip both primary and secondary of the trafo during overcurrent? or primary bkr alone would be sufficient?
The reason why I said primary alone instead of secondary is: I have another trafo with same rating but secondary main circuit bkr is not provided where as only the feeder distribution bkrs are provided. I cannot keep on tripping all the secondary feeder bkrs and MV bkr, which is not economical is what I think. So, please advise. Thanks in advance