I am installing a 175 kva transformer but only need 80 amps on the secondary. Can I protect the primary at 200 amp? It is three phase
Only 200A available by load calculations or by upstream OCPD?I only have 200 amps available on the primary
I'm inclined to agree. Unless some kind of current limiting like a soft start is used.Given the specs on the transformer and breaker, an engineer could confirm but I have serious doubt a 200 amp breaker will handle the inrush current of a 175kva @ 208.