Maybe we could ask Smart $ to slow down his avatar by a factor of 10 or so?
I have seen a larger version of his avatar posted before, maybe I can find it?
I guess I should have added that since a three phase transformer that can supply a 120 volt load equally across all three phases will be a Wye 208/120, and if you figure the current at 208 volts you will get the 50 amps each single phase load will pull, 18,000/208/1.732 = 49.96 amps or 50 amps because of the rounding off in the equation.
When figuring the current of a transformer you must use the line to line voltage to get the correct current rating of the transformer, in my other post above I was figuring a line to line voltage of 120 volts for the three phase which might lead to some confusion since a transformer with this voltage would not be a commonly made transformer, calculating for a delta transformer with a center tap between A and C can even complicate things a little more because the line to neutral loads will not balance across all three phases as they are only connected from A to neutral and B to neutral, in this case you must figure your single phase line to neutral loads separately, then figure in the current with your other line to line loads to find the rating of the transformer needed or just add up the kva of all the loads to know what size transformer you need.
Lets say you have 18kva worth of loads that are line to neutral, this will place 75 amps between A and C phase or 9kva from A to neutral and 9kva from C to neutral and since these are equally balanced loads the neutral will not see any current, now add in two more 18kva 240 volt loads one between A and B and one between B and C, just to keep things balanced, if we add up the three 18kva figures we get 54kva, so we can take this figure to find our current each phase will see by 54,000/240/1.732 = 129.9 amps or 130 amps per phase the next size up common sized transformer will be a 75kva (unless they do make a 60kva which I have not seen other then a special order) which will provide 180.4 amps per phase so you will end up with 50.3 amps per phase extra for future loads, again this is only for a 4-wire delta with a high leg (B phase) but some of the math will apply to other three phase transformers also such as a 208/120Y when you have 120 volt loads only connected between two of the phases which would be uncommon, generally you would figure any balanced line to neutral loads at the 208 volt rating to get the phase current on the highest loaded phase to get the correct rating of the transformer needed, of course there are other figures you must use to find the correct kva rating the transformer will see such as the power factor rating and the transformer efficiency or the transformer impedance which will add to the size of the transformer needed for a given set of loads, but in trying to keep it simple as I can see that the OPer is struggling to wrap his head around this I was trying to keep it to the basics, once we see the OP has got this part down we can teach him how to add PF and transformer impedance or efficiency to the end results to figure how to size the transformer correctly which is the simple part.