I was trying to install a ring door bell today and think I fried the unit. I installed a 120v to 16v transformer as instructed but the front bell started smoking. When I put my meter on the transformer line side, I showed 122V. On the load side it was 21.8V. Did I get a bad transformer? This seems way to high for a supposedly 16V transformer. Any ideas are appreciated.