Back in the days of 110/220 volts, we called the high-leg 190v.What system is the POCO providing? 190 volts to ground doesn't sound right, how do you know that the phase to ground voltage is 190 volts?
Is that applicable in 2021?Back in the days of 110/220 volts, we called the high-leg 190v.
agreeYou're looking for a 240D-to-208/120Y transformer.
Does not make much difference what he has as long as it's 240 phase to phase but I agree with Infinity there is still some question on the service. He states "3 phases.no neutral" so it sounds as if it might be a ungrounded.Back in the days of 110/220 volts, we called the high-leg 190v.
You're looking for a 240D-to-208/120Y transformer.
Back in the days of 110/220 volts, we called the high-leg 190v.
Whadja say, Sonny?OMG!!
Just how old are you???
![]()
Well I have heard about it, but don't "remember it" as in I was there... Wasn't that like in the 30's or before when it went from 110/220 to 120/240?Whadja say, Sonny?![]()
I'll be 66 in May. I can't be the only one who remembers this.
Whadja say, Sonny?![]()
I'll be 66 in May. I can't be the only one who remembers this.
Red leg delta, orange leg service.. so many different names it’s kind of hard to keep up with what electricians want with all the different names depending on where they are from.May be regional also... it was "190" here for a while also. Us ole timers rememeber "190" and the whipper snappers don't even know what a "wild leg" or "stinger" reference is![]()
Yes the system is 3 phase the high leg is marked yellow and the system has no neutral . Was looking to install a transformer and bring it to 120 /208 with neutral. .yes the building is extremely old old rubber factory in NJ
Are you sure you have a high leg system? The neutral is always part of a high leg system.Yes the system is 3 phase the high leg is marked yellow and the system has no neutral . Was looking to install a transformer and bring it to 120 /208 with neutral. .yes the building is extremely old old rubber factory in NJ