Transformer question

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have been asked to generate a 240/120V split phase circuit from 480/277V. I'm thinking that I will connect the primary of a 480V to 240V split phase transformer to two phases of the 480/277V without the neutral; is that correct? Does anyone make a transformer like that with no neutral on the primary side or can I just leave the primary neutral floating?
 
This is similar to what you're looking for only difference is that the output is straight 240 volts. You would connect the neutral where the system bonding jumper is installed to get 1Ø, 120-240.120-240 Transformer.jpg
 
This is similar to what you're looking for only difference is that the output is straight 240 volts. You would connect the neutral where the system bonding jumper is installed to get 1Ø, 120-240.View attachment 2581688
Now that you mention it, I'm not sure the customer needs the neutral on the secondary side; I will check. FMI, how many kVA is that tranny? Y and O are primary, R and B are secondary? The SBJ is connected to the mid point on the secondary between the two coils, correct?
 
I have been asked to generate a 240/120V split phase circuit from 480/277V. I'm thinking that I will connect the primary of a 480V to 240V split phase transformer to two phases of the 480/277V without the neutral; is that correct? Does anyone make a transformer like that with no neutral on the primary side or can I just leave the primary neutral floating?
Primary will not need a neutral, all you need is two phases on the primary. No neutral pulled with the feeder, just the egc, which would just go to the transformer frame.
 
Now that you mention it, I'm not sure the customer needs the neutral on the secondary side; I will check. FMI, how many kVA is that tranny? Y and O are primary, R and B are secondary? The SBJ is connected to the mid point on the secondary between the two coils, correct?
Yes, 480 volts in, 240 volts out. 50 kva. This should be the nameplate.

f13010ec-8dea-473d-9c9d-6b3294d15eae-1_all_13506.jpg
 
Doesn't the NEC requires you to bond systems to <150 L-G when possible? If it is a possible connection, per the nameplate, is that sufficient?
 