I assume you are talking the originating system X0, as he said there was no xfmr X0.brian john said:SMART:
Not necessarily, if this is a buck boost, the XO and HO are common and therfore tihs is not a SDS.
You are correct if one wants the derived system to not be "separately" derived. Simply connect the 208 system neutral to 480/277V secondary neutral (H0). Still, with this connection to H0, no ground detector needed.
In either case, buck-boost is not the appropriate term for the setup. It will either be a derived system or a separately derived system. For a derived system, the primary feeder will consist of L1, L2, L3, N, and EGC. There will not be an SBJ. For a separately derived system, the primary feeder will consist of L1, L2, L3, and EGC, and an GEC (the GEC and EGC can be possibly one appropriately-sized and connected conductor) then an SBJ.