Here is a transformer I saw today in a metal fabricaion shop.
3 phase 460 delta primary, 230/133 Y secondary (see nameplate.) It has been in operation for several years. 35' secondary conductor length.
Loads are 3 ph. 230v. only.
Secondary overcurrent protection are fuses in a fuseblock bolted to the inside of the transformer.
LV conductors are color coded the same as the HV.
Xo is not bonded and there is a sign near the secondary terminals "do not ground"(see photo). What was the reasoning for this? A ground fault would energize the machinery, conduit, etc.
http://i158.photobucket.com/albums/t108/buck33k/009.jpg
http://i158.photobucket.com/albums/t108/buck33k/007.jpg
http://i158.photobucket.com/albums/t108/buck33k/006.jpg
3 phase 460 delta primary, 230/133 Y secondary (see nameplate.) It has been in operation for several years. 35' secondary conductor length.
Loads are 3 ph. 230v. only.
Secondary overcurrent protection are fuses in a fuseblock bolted to the inside of the transformer.
LV conductors are color coded the same as the HV.
Xo is not bonded and there is a sign near the secondary terminals "do not ground"(see photo). What was the reasoning for this? A ground fault would energize the machinery, conduit, etc.