R2006

Member
Location
PENNSYLVANIA
Hi everyone.

Its Friday and i am brain dead from the week and drawing a blank for some reason so a little help please. Have a piece of equipment to hook up, existing disconect is 3-phase 218v 100 amp, to a step up transformer on equipment which is 400v 3-phase 33 amps. willl the 100a disconnect handle this load.
Thanks for any help.
 
3 phase 218 volt strange but...

equipment 400 v 3 phase at 33 amps
(400 x 1.732 x 33 = 22.9 kw) or as ibew501ed states, a minimum of a 30- kva transformer
218 at 100 amps would be 37 kw so it would supply the load but the inrush on the transformer will probably cause breaker tripping.
basically as he says close
 