Transformer Question
brian john
Kilmarnock, Va
Retired after 52 years in the trade.
I have an unusual transformer (see picture) This is an Allis-Chalmers 150 KVA Dry Type transformer there are two visible coils and the drawing appeas to be a T. This is 3 phase 480 VAC to 208/120 VAC. There was an issue with the output voltage and just trying to get some information. Any help would be appreciated.
We plan to megger and TTR the transformer.
From what I see A and C are derived from one coil and the neutral and B phase from a sperate coil.
Lousy picture taken with my IPhone.
My guess... The diagram was just badly drawn (in other words a "delta" and "wye" configuration were not correctly represented).
As for the strange voltages I'll ask the stupid question... did anyone look at the positions of the primary taps?
Pete
This is definitely a T connected transformer.
This construction is very common on small (i.e. <30kVA) units, I cannot say I have seen one at the 150kVA size.
I would have to confirm it, but I believe you would treat it as a wye-wye transformer during your TTR.
And it weights 1,400 LBS a nominal weight for a delta wye is 900-1000 LBs. But this is old maybe the steel was not up to todays standard?
It appears you cannot get to the T connection and with twwo wound coils just threw me and I cannot locate anything on line.
Based on the location of XO it seems there is a difference in the ratios of the coils.
Yes there is a difference.
I just pulled out my TTR book and it does have a procedure for testing T-Type transformers. It looks like you apply some external jumpers between the coils and then test each coil as if it was single phase.
Thanks Jim
Interesting read
and it seems a T-T must have extra weight (copper steel) by design.
http://www.hammondpowersolutions.com/upload_files/hpsi-ta11.pdf
A Scott (Tee) connection is for going between 2-phase and 3-phase.
A standard T connection is for 3-phase to 3-phase.
They are not the same arrangements, even though they look similar. In particular there is a difference in the connection point of the teaser winding while both have a primary tap at a 86.6%, the standard T requires a tap at about 33% on the secondary (this becomes the X0).
What I did, We ttr'd the transformer and meggered it. Then I applied 208 on the primary from a 15 amp fused safety switch, using a variac to minimize inrush current, blowing my fuses. What I found out someone a long time ago mis-marked the secondary terminals. XO was marked X3, X3 was marked XO X1 and X2 were tagged correctly.
Seems 120 VAC appliances do not appreciate 208 VAC.