kingb,
You cannot find the calculations that I did because I did not post them. I posted a description of the physical system that pointed to the results that I got, and I posted the results, but I did not 'show my work'.
Rattus presumably checked my results by doing his own calculation, and steve66 posted both the inputs and results from a particular piece of software, which agree with the answer that I gave.
This does not mean that I believe that symmetrical components is an incorrect way to solve this problem, far from it. The method of symmetrical components is probably the most efficient way to solve these problems when designing real systems. However this is _not_ the only method to use, and for this exceedingly simplified and explicitly unbalanced example, other methods provide the answers more simply and with less chance of error. Basic vector math may be used. The approach of examining each and every circuit, figuring the vector current for each circuit, and then adding these up would not scale well to a full system design, but it is a correct approach.
Somewhere in your calculations, the necessary information that the system is not balanced is being lost. I presume that this is an error in the software that you are using, because the method of symmetrical components should be able to deal with this.
To answer your question above:
kingpb said:
How can you possibly say that a 10A load @208V = 2080W, or 2080VA w/ pf=1, and a (2) 10A loads at 120V = 2400W or 2400VA w/ pf=1 are going to have the same current draw of 2.5A at 480V.
There is a trick in the question: the power factor of 1. The _load_ has a power factor of 1, meaning that the current through the load is in phase with the voltage difference between terminal A and terminal B of the transformer. But the current through the coils of the transformer is _not_ in phase with the voltage developed across the coils of the transformer.
We have three voltages to consider Vab, Van and Vbn. These are 208V, 120V, 120V respectively. These are each at their own phase angle. I_load is in phase with Vab, and thus not in phase with Van nor with Vbn.
In both the 10A 208V example, and the dual 10A 120V example, you have 10A going through the two secondary coils, and thus 2.5A though each primary coils. This is true in both cases. However the phase angle of the current flow, and thus the power factor, is different between the two cases, and in neither case is the power factor actually unity on all of the supply conductors.
-Jon