In the 2002 code 450.21(B) a room must be fire rated (1 hour) if a dry type transformer larger than 112.5 KVA is installed in it. Exception No. 2 allows transformers larger than 112.5 KVA installed in an un-rated room if the transformer has a class 155 insulation system and enclosed except for ventilation openings. The transformer manufacturer I am looking at does not have a class 155 rating, however it does have a class R rating which has a 220 deg C insulation system with 150 deg C temp rise. Does the class R rating of the manufacturer (Cutler Hammer) meet the Class 155 rating refered to in the code? Is there a cross reference between these class type insulation systems somewhere? I do not have access to the ANSI/ASTM-1995 or NFPA 251-1999 refered to in the FPN in this section.