ken44
Senior Member
- Location
- Austin, TX
I have a 150KVA transformer that is located inside a Power Distribution Unit (PDU), made by Liebert, the PDU has 4-42 circuit panels and each panel is fed by 250MCM (255 Amps, 75 Degree Column), the name plate rating is 277/480Volts Input/186Amps, the Output is 120/208Volts/417Amps. I have a few questions concerning this that have arisen over the years but I have'nt concluded that anyone to this point has actually given me a satisfactory answer.
1. Is the 417 Amps output per phase or total? I thought is was total based on 150KVA/360=417Amps
2. Even if the answer is 417 Amps per phase, thats only 1251 Amps total and with 168 circuit breakers available and if each one were only 20 Amps this would be a potential load of 3360 Amps or 2688 at 80% which still seems to be way off.
Load Calculation: The customer needs 100 each of NEMA L6-20 circuits (208V/20A/2Pole), 78 each of NEMA L6-30 circuits (208V/30A/2Pole) and 5 each of Russellstol 208V/50A/3Pole circuits and they need redundant feeds, this requires 380 circuit breaker spaces but with redundant feeds (190 circuits from 2 power sources) it gets a little more complicated because I only have capacity for 168 spaces in each PDU so I understand that they will either need another PDU or two or will have to give up some of their rendundancy. I would also appreciate any insight that someone may have about the load calculation.
1. Is the 417 Amps output per phase or total? I thought is was total based on 150KVA/360=417Amps
2. Even if the answer is 417 Amps per phase, thats only 1251 Amps total and with 168 circuit breakers available and if each one were only 20 Amps this would be a potential load of 3360 Amps or 2688 at 80% which still seems to be way off.
Load Calculation: The customer needs 100 each of NEMA L6-20 circuits (208V/20A/2Pole), 78 each of NEMA L6-30 circuits (208V/30A/2Pole) and 5 each of Russellstol 208V/50A/3Pole circuits and they need redundant feeds, this requires 380 circuit breaker spaces but with redundant feeds (190 circuits from 2 power sources) it gets a little more complicated because I only have capacity for 168 spaces in each PDU so I understand that they will either need another PDU or two or will have to give up some of their rendundancy. I would also appreciate any insight that someone may have about the load calculation.