For 15kV to 480V AND for
15kV to 4160V
On dry type transformers we've got the following ratings available.
OA/FA where OA = Open Air and FA = Fan Cooled. The difference is 33.3 percent capacity. But how's it work when you add 55/65 deg ratings correct?
What do you get e.g. OA/FA/??
For liquid types, what's the increase with fans? Is it still 33%? And again what different ratings are available if you combine temp rating with fan ratings?
Thanks,
15kV to 4160V
On dry type transformers we've got the following ratings available.
OA/FA where OA = Open Air and FA = Fan Cooled. The difference is 33.3 percent capacity. But how's it work when you add 55/65 deg ratings correct?
What do you get e.g. OA/FA/??
For liquid types, what's the increase with fans? Is it still 33%? And again what different ratings are available if you combine temp rating with fan ratings?