chevyx92 said:So then I theoretically I would need a single phase disconnect because only 2 of the phases would have fused protection and the 3rd phase (grounded phase) with white tape would pass through my disconnect? Correct???
Yes that is one way but I do agree with Don that you better be sure of the listing.
Another way to do this is a 3 phase fused disconnect but on the grounded phase you install a 'dummy fuse'. Bussman sells listed 'non-fuse gizmos' to install in the grounded phase position.