Transformer Secondaries

Status
Not open for further replies.

domeng

Member
Does the NEC require a single protection device for secondary feeder from a transformer to a Power Panel if the feeder is less than 10 feet?
 
Electrical Consultant

Electrical Consultant

:confused:
Article 450 deals with protecting the transformer.

As Karl mentioned, Article 240 is for conductor protection.

My basic question is do I need a single protective device or are multiple protective devices acceptable?This is not a network transformer and primary protection may not be sized to protect the secondary conductors
 
Good reference. I had forgotten about that one. Funny we see transformers we go to 450 and secondaries to 240.21 and forget about certain "Key Words" as in feeding a "PANELBOARD"...408

Thanks Chris!

Your welcome.

I agree, sometimes we don't think about what the transformer is feeding and just look at 240.21(C) and 450.3(B).

Chris
 