Hey guys,
Think this has been discussed before, but still a little confused. Say i have a 150kVA delta-wye, 480-208V transformer. I am using primary and secondary protection. How would I size my secondary side circuit breaker and conductors? I?m getting confused between articles 240.4(B), 240.21(C), and table 450.3(B).
Based on previous projects others have done, for a 112.5kVA secondary side they use:
Circuit breaker = 350A
Secondary conductors = (4) #500kcmil + (1) #1/0 gnd
Here is my approach:
FLA of a 112.5kVA transformer secondary = 312A
Circuit breaker size is 312 x 125% which = 390A. Table 450 says to round up, so would it be a 400A?
Secondary conductors would be #600kcmil. 600kcmil is rated for 420A. How does article 240.21(C) come into play here?
Thanks for any suggestions.
Think this has been discussed before, but still a little confused. Say i have a 150kVA delta-wye, 480-208V transformer. I am using primary and secondary protection. How would I size my secondary side circuit breaker and conductors? I?m getting confused between articles 240.4(B), 240.21(C), and table 450.3(B).