I have a transformer that's 3 phase, 225 Kva, 480: 208/120. The transformer secondary conductors are landed on an 800 amp molded case switch inside a chiller. On the load side of the switch it splits to two 400 amp circuit breakers.
The chiller nameplate isn't stamped with an MCA or an MOP unfortunately. Following the manufacture's procedure for calculating MCA and MOP I came up with 514 amps @ 208 VAC and 624 amps for the MOP with the next size down being 600 Amps.
Currently this transformer is connected with parallel (two conductors per phase) 300 kcmil (combined ampacity of 570 amps).
A few things I'm concerned about. In meeting the MOP requirement, the manufacturer provided the 800 amp switch with the two 400 amp circuit breakers so I'm assuming that's correct. I would have thought installing a separate over current device at the chiller's listed MOP as redundant. The manufacture already provided over-current protection. Is an additional external over current device needed to meet the NEC MOP requirement?
In this case with the parallel 300 kcmil conductors landed on the 800 amp molded case switch. I can't find a section this could be okay under considering the conductors are coming off the secondary of the transformer. Even though the conductors meet the MCA I'm thinking they need a minimum ampacity of 800 amps. Thoughts? Something I'm missing?
Just for reference the primary overcurrent protection is 600 Amps.
The chiller nameplate isn't stamped with an MCA or an MOP unfortunately. Following the manufacture's procedure for calculating MCA and MOP I came up with 514 amps @ 208 VAC and 624 amps for the MOP with the next size down being 600 Amps.
Currently this transformer is connected with parallel (two conductors per phase) 300 kcmil (combined ampacity of 570 amps).
A few things I'm concerned about. In meeting the MOP requirement, the manufacturer provided the 800 amp switch with the two 400 amp circuit breakers so I'm assuming that's correct. I would have thought installing a separate over current device at the chiller's listed MOP as redundant. The manufacture already provided over-current protection. Is an additional external over current device needed to meet the NEC MOP requirement?
In this case with the parallel 300 kcmil conductors landed on the 800 amp molded case switch. I can't find a section this could be okay under considering the conductors are coming off the secondary of the transformer. Even though the conductors meet the MCA I'm thinking they need a minimum ampacity of 800 amps. Thoughts? Something I'm missing?
Just for reference the primary overcurrent protection is 600 Amps.