Transformer secondary conductors

Merry Christmas
Status
Not open for further replies.

jkrauss

Member
My question is what is permissible length of transformer secondary conductor without over current protection? the transformer is a Y step down 480 / 120/240 volt it is in a commercial building is is feeding a main breaker receptacle panel , the panel is at least 80 feet from the transformer . I read under 240-21c the length cannot exceed 10 feet with out protection. Am I right?
 
It's possible with the right size conductors and over-current devices that you could qualify for 25ft under 240.21(C)(6), but as a general rule, 10ft is most common.
 
If secondary conductors are outside except for load termination, distance is unlimited [240.21(C)(4)].
 
If secondary conductors are outside except for load termination, distance is unlimited [240.21(C)(4)].

Are you a salesman? :) You pointed out the good without pointing out the rest.

There is a good deal more to it than just being outside but yes it is possible.
 
Are you a salesman? :) You pointed out the good without pointing out the rest.

There is a good deal more to it than just being outside but yes it is possible.
Yep! ...just covering possibilities without evidence to the contrary. :D
 