Am i correct that i can run over 25ft with secondaries if primary OCPD is less than 125% of primary full load current.
I am looking to install a temp 100-KVA transformer 208V primary 277/480V secondary to feed a 480v 600-amp panel feed with parallel 300MCM copper.
If i fuse primary 208v feed at 300-Amp im less then 125%, can i supply the seconday 125' to panel without over current protection?
Where the primary overcurrent protective device does not exceed 125 percent of the primary full load current, secondary overcurrent protection for the transformer is not required. An allowance is made to go to the next larger standard size of fuse or circuit breaker where 125 percent of transformer full load current does not match any of the standard sizes shown in 240.6.
I am looking to install a temp 100-KVA transformer 208V primary 277/480V secondary to feed a 480v 600-amp panel feed with parallel 300MCM copper.
If i fuse primary 208v feed at 300-Amp im less then 125%, can i supply the seconday 125' to panel without over current protection?
Where the primary overcurrent protective device does not exceed 125 percent of the primary full load current, secondary overcurrent protection for the transformer is not required. An allowance is made to go to the next larger standard size of fuse or circuit breaker where 125 percent of transformer full load current does not match any of the standard sizes shown in 240.6.