Transformer Secondary Over Current Protection

Status
Not open for further replies.

brian john

Senior Member
Location
Leesburg, VA
Have a situation where a customer has the following installation

150 KVA 480-208/120, 3 phase Delta/wye transformer with the following

PRIMARY
200 amp circuit breaker over current protection
3/0 copper conductors
SECONDARY
4-200 amp fusible safety switches with 175 amp fuses
2/0 copper conductors

In regards to the secondary over current protection what is the maximum size fuse that can be installed in each device.

the maximum single device would be 600 amps (125% of 416 A=520)

Do we take the 520 amp and divide by 4 or am I totally off base?
__________________
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You are fine as is. The transformer (primary & secondary windings) are protected per 450.3(b) as the primary overcurrent is less than 125%.
The only thing you need to watch from there is protection of secondary conductors per 240.21(C) and the 2/o is rated 175 amps.
The total secondary OCP is not relevant to the transformer protection as the primay OCP has that covered..
 