brian john
- Kilmarnock, Va
- Retired after 52 years in the trade.
Have a situation where a customer has the following installation
150 KVA 480-208/120, 3 phase Delta/wye transformer with the following
PRIMARY
200 amp circuit breaker over current protection
3/0 copper conductors
SECONDARY
4-200 amp fusible safety switches with 175 amp fuses
2/0 copper conductors
In regards to the secondary over current protection what is the maximum size fuse that can be installed in each device.
the maximum single device would be 600 amps (125% of 416 A=520)
Do we take the 520 amp and divide by 4 or am I totally off base?
__________________
PRIMARY
SECONDARY
__________________