dpb
Member
- Location
- Cleveland, Ohio
- Occupation
- Electrician
Hello, I haven't done a whole lot of transformer hook ups so i wanted to make sure i have this correct. I'm installing a 14kva step up 208D to 480Y transformer and wanted to make sure that i am interpreting 240.21 C 1 correctly. The primary is protected at the box with a 40a, and will have a disconnect immediately before the transformer on the primary side. the load side will have minimum 12awg conductors and will only feed one device mounted right next to the transformer (less than 5 feet away). So with that information i would not need a disconnect or overcurrent protection on the secondary, correct? device on the 480 side is a 13.6 max amperage forklift charger
208x40=8320w
8320/480=17.33a
13.6x1.25=17a
208x40=8320w
8320/480=17.33a
13.6x1.25=17a