VxA
Member
- Location
- Atlantic Provinces (Canada)
Hi,
This application is a 13.2/4.16kV 3-Phase Delta-Wye transformer feeding a Medium Voltage MCC line-up in an industrial (supervised) facility. The transformer is oil filled (outdoor).
The location of the transformer is such that I would need to run the secondary conductors outside for 50' or so (they will be physically protected as per NEC). Then I would like to enter the electrical room and run for 25ft or less to the proposed location of the Medium Voltage MCC.
The primary protection (which is tied into secondary side ground fault detection to allow for quicker reaction in event of secondary ground fault) keep the Arc Flash levels quite low (Cat 1). As a result, I would like to not have incoming protection on the MV MCC and simply let the individual cubicle fused disconnects do the job. There are 5 such fused disconnect switches.
Questions;
1) because the overall secondary run is > 25ft, am I able to avoid having secondary protection installed outdoors (or at nearest indoor location to the conductor entrance)? Sections 240.21(C) (3) & (4) talk about this. It is an industrial application.
2) if questions (1)'s answer is yes, can I avoid having incomng protection on the MV MCC so long as I use 6 or less individual OCPDs in the MCC, and I size the secondary conductors such that they are protected by the OCPDs? Section 450.3(A) discusses this.
Your help would be appreciated.
Thanks,
This application is a 13.2/4.16kV 3-Phase Delta-Wye transformer feeding a Medium Voltage MCC line-up in an industrial (supervised) facility. The transformer is oil filled (outdoor).
The location of the transformer is such that I would need to run the secondary conductors outside for 50' or so (they will be physically protected as per NEC). Then I would like to enter the electrical room and run for 25ft or less to the proposed location of the Medium Voltage MCC.
The primary protection (which is tied into secondary side ground fault detection to allow for quicker reaction in event of secondary ground fault) keep the Arc Flash levels quite low (Cat 1). As a result, I would like to not have incoming protection on the MV MCC and simply let the individual cubicle fused disconnects do the job. There are 5 such fused disconnect switches.
Questions;
1) because the overall secondary run is > 25ft, am I able to avoid having secondary protection installed outdoors (or at nearest indoor location to the conductor entrance)? Sections 240.21(C) (3) & (4) talk about this. It is an industrial application.
2) if questions (1)'s answer is yes, can I avoid having incomng protection on the MV MCC so long as I use 6 or less individual OCPDs in the MCC, and I size the secondary conductors such that they are protected by the OCPDs? Section 450.3(A) discusses this.
Your help would be appreciated.
Thanks,