For xfrmr secondary currents less than 9 amps, you can protect at 167%.That would be 15amps.The minimum size conductor would be 14 awg.IMO anything less than 15a is a non standard rating. I don't think anyone would want an 18 awg wire on their xfrmr, so they set the rating @ 167%.
Rick