ron
Senior Member
- Location
- New York, 40.7514,-73.9925
The need for it or not is always a problem for me.
This is an existing condition:
175A-3P CB serving a 112.5kVA 480 delta - 208/120V wye transformer.
The secondary of the transformer has 1 set of 4-500kCMIL + GND running up a high rise building (no secondary protection for the transformer).
There is (4) 100A fused switches tapped off the 500kCMIL riser in the upper portion of the building each serving 100A panelboards.
Is this okay?
What if a 5th 100A fused switch was added?
The primary protection is the next size higher than 125% of the primary 135 FLA, so is primary protection only okay? Since it is a delta wye, the NEC says that it can't be protected by primary only.
This is an existing condition:
175A-3P CB serving a 112.5kVA 480 delta - 208/120V wye transformer.
The secondary of the transformer has 1 set of 4-500kCMIL + GND running up a high rise building (no secondary protection for the transformer).
There is (4) 100A fused switches tapped off the 500kCMIL riser in the upper portion of the building each serving 100A panelboards.
Is this okay?
What if a 5th 100A fused switch was added?
The primary protection is the next size higher than 125% of the primary 135 FLA, so is primary protection only okay? Since it is a delta wye, the NEC says that it can't be protected by primary only.