Is that 125% from Table 450.3(B)? If so then the next size up rule would permit a 125 amp OCPD.The 83.3 should then be multiplied by 125%. So 100 amp OCPD would be appropriate.
Next size up is 110A.Is that 125% from Table 450.3(B)? If so then the next size up rule would permit a 125 amp OCPD.
You're right I forgot about 110.Next size up is 110A.
The issue I'm having is you can't get more than 83 amps out of the 30 kVA transformer. So when someone sees 150 amp main breaker on a panel connected to the transformer secondary, they are probably assuming the panel handle 150 amps of non continuous load.
So if it's not a code issue, isn't this a really bad design issue then?
You would need a panel board rated 500 amps or above to comply with 408.36. would certainly be kind of a strange design, but I don't see any issue whatsoeverLet's say instead of a 150 amp MCB, there's a 500 amp MCB in the panel connected to the transformer secondary with 600 kcmils and no code issues - right? How could this be allowed on a 30 kVA transformer secondary??
Let's say instead of a 150 amp MCB, there's a 500 amp MCB in the panel connected to the transformer secondary with 600 kcmils and no code issues - right? How could this be allowed on a 30 kVA transformer secondary??
I agree with your question something just seems wrong about it. In your example you would need to use a 400 amp OCPD with the 600's not a 500 amp.Let's say instead of a 150 amp MCB, there's a 500 amp MCB in the panel connected to the transformer secondary with 600 kcmils and no code issues - right? How could this be allowed on a 30 kVA transformer secondary??
Because the main or OCPD ahead of the panel won't allow you to overload the panel.How can it be allowed to have 40 spaces in a 200 amps panel where you can put 800A worth of 20 amp breakers in there, not to mention sizes larger than 20?
Agree - should have been 400 amp in example. I'm going to fix thatI agree with your question something just seems wrong about it. In your example you would need to use a 400 amp OCPD with the 600's not a 500 amp.
Correct (that was a rhetorical question btw).Because the main or OCPD ahead of the panel won't allow you to overload the panel.
Huh? Certainly not.I read the section as saying that the presence of secondary protection, whether that is the form of a panelboard MCB or fused disconnect for a nonmotor load, requires you to size it to 125% of the transformer's rating.
Huh? Certainly not.
Table 450.3(B) says that if the primary OCPD is sized to at most 125% (rounding up to a standard size is allowed), secondary protection is not required, so you can use whatever size you want. If you size the primary OCPD higher, then it must be at most 250% (no rounding up), and you must provide secondary OCPD of at most 125% (rounding up allowed).
As a practical example, say I have a 50 kVA transformer on hand, and it will work in the short run, but my expansion plans will require upsizing it to 150 kVA, which is on order with a long lead time. I can install primary and secondary conductors and a secondary panelboard and OCPD sized for 150 kVA (using either option in Table 450.3(B)), as long as I size my temporary primary OCPD for 125% of the 50 kVA. Then when I change transformers, I just need to change the primary OCPD, nothing else.
Cheers, Wayne