But you make the idea that it is still required seem like a plausible reading. It is not.
(2020 NEC) 450.3(B) says "Overcurrent protection shall be provided in accordance with Table 450.3(B)." The title of Table 450.3(B) is "Maximum Rating or Setting of Overcurrent Protection for Transformers . . .". When the table entry says "Not required" that means there is no maximum. Any other reading is implausible.
Cheers, Wayne
I didn't say transformer secondary protection was required.
I said where secondary protection is installed, it is required to meet the table's second row. That is my interpretation of it.
Where it states the type of protection installed, it specifies "Only Primary" and "Primary and Secondary". So, I read that as, where secondary protection is installed, it is both "Primary and Secondary" and needs to meet that requirement. There are only a few applications where secondary protection is not installed. So in the case of a panelboard, I would argue that the protection for the panelboard would need to suffice in meeting 408.36, 450.3's "Primary and Secondary" protection, along with 240.21(C), because that OCPD now has an overlapping job. It is common for one OCPD to be for more than one reason and need to met requirements of more than one section.
No different to when a wire-type EGC is installed. You then have to meet the rules for 250.122. You wouldn't ignore them just because a wire type isn't needed since you already have EMT or other means. If it is installed, you have to meet the requirements for a wire type EGC.
I see it as the same for table 450.3.
Where Primary and Secondary protection exist, you have to meet the second row. Where there is an application that requires only primary protection, you wouldn't have any OCPD on the secondary side of the transformer.
And, in temporary applications, I believe you have some allowances for temporary oversizing. Especially if all the load isn't installed yet. I would hope the AHJ would make an exception. But I don't think anyone is arguing that a 30kVA transformer's secondary windings, bushing, terminations, would hold up being protected by a 400A MCB and 400A panelboard. That seems frivolous to me. The transformer will obviously fail provided a sustained load of 300A. I would need to see the argument that the primary side is capable of protecting it. From my understanding, the heat in the secondary is not always translated to the primary since they are magnetically coupled. I have also had a few calculations where a large unbalance single phase load could overload the wye side's LV terminal of a phase before the resultant line current in the delta high side would trip.
So to argue that, where secondary side protection is required (delta - wye), but the primary side is sized to "Primary only" of 125%, means you could then size the secondary side to anything is just bad engineering practice and, in my opinion, a misinterpretation of 450.3. The primary side is not going to suitably protect against overload on the low voltage side wiring or terminations. That is my understanding for the existence of 240.21(C).